UPS Sizing

Jim B elemint at gmail.com
Mon Aug 22 12:16:28 MST 2005


Something I like to use is the apc selector which helps to determine which 
ups would work and how much power is required for the device in question.

go to http://apc.com/tools/ups_selector/index.cfm and then select "Configure 
by Devices" The click "PC/Workstation" then pick out your pc and then select 
add to configuration and then will see what power is required for the device 
and just continue on with the process and you will see what apc recommends.






Jim



On 8/21/05, Joseph Sinclair <plug-discuss at stcaz.net> wrote:
> 
> AC doesn't work quite as simply as VoltsXAmperes=Watts, because AC is 
> constantly changing in amplitude, we have to apply some averaging equations 
> to get the actual watt load (usually, this is the simple RMS equation, but 
> it's much more complex when there are multiple phases, or the load is 
> non-linear).
> That's why UPS units are sold by VA, not Watt. As long as the VA rating is 
> greater than VoltsXAmperes you should be just fine for household AC. To 
> determine runtime on battery, you should use the manufacturer's "typical" 
> load (in watts) for the computer, and compare against the UPS manufacturer's 
> chart.
> 
> ==Joseph++
> 
> P.S. your manufacturer specs suggest that the *maximum* load for your G5 
> would be 125X7.5=938 VA, typical load is probably around 800VA at 115V. A 
> 1200VA unit should easily accommodate the computer, provided nothing else is 
> connected that exceeds 250VA additional load.
> 
> Craig White wrote:
> > Trying to figure out UPS size for a G5 (not that it matters).
> >
> > According to Apple's Specifications on a G5
> >
> > Maximum current: 6.5A (low-voltage range) or 7.5A (high-voltage range)
> > for 100-125V AC, 3.5A for 200-240V AC
> >
> > A Belkin F6C1200-UNV
> > <http://catalog.belkin.com/IWCatProductPage.process?
> > Merchant_Id=&Section_Id=76&pcount=&Product_Id=199025>
> >
> > 1200 VA unit has stated capacity of 670 watts.
> >
> > Now my simple math says 7.5A x 115V is 862.5W which would suggest that
> > this system is not sufficient for a G5
> >
> > Is this correct?
> >
> > I would need something at least 1500VA?
> >
> > Craig
> >
> > ---------------------------------------------------
> > PLUG-discuss mailing list - PLUG-discuss at lists.plug.phoenix.az.us
> > To subscribe, unsubscribe, or to change you mail settings:
> > http://lists.PLUG.phoenix.az.us/mailman/listinfo/plug-discuss
> >
> ---------------------------------------------------
> PLUG-discuss mailing list - PLUG-discuss at lists.plug.phoenix.az.us
> To subscribe, unsubscribe, or to change you mail settings:
> http://lists.PLUG.phoenix.az.us/mailman/listinfo/plug-discuss
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.plug.phoenix.az.us/pipermail/plug-discuss/attachments/20050822/91f8ecf7/attachment.htm


More information about the PLUG-discuss mailing list